Re:Why we ground electrical systems (2015)
by jessaustin on Friday August 02, 2019 @05:21PM
(#20596750)
TFA is a bit more abstract than you realize, and perhaps that abstraction could mislead the unwary. It is technically correct, but makes a distinction you've missed. If a gremlin cuts the (green) wire between my breaker box and my ground rod, the system is no longer "grounded to Earth", so it wouldn't handle lightning strikes well. However, the "EGC" in every house circuit is still bonded to neutral at the box, so breakers will still trip when the wire inside my clothes dryer rubs against the metal body. That is the function of the EGC. The EGC itself does nothing to protect against transient earth potentials like lightning strikes. That is the job of the grounding rod etc. Just because both wires are green, doesn't mean they're doing the same thing.
Re:Why we ground electrical systems (2015)
by wrycoder on Friday August 02, 2019 @09:48PM
(#20598119)
In the USA, there's no green wire between the service panel and the ground rod. The green wires end at the ground bus in the panel, which is bonded to the panel case. A heavy, bare copper wire leads from the ground bus to the ground rod.
The neutral bus is either bonded to the case with a green grounding screw or is integral with the ground bus.
> Marvelous explanation.
It might be Marvelous, but it's not actually true. The ground wire IS connected to the earth!
I don't want to be rude, but I think the OP should take this post down, it has a LOT of mistakes.